So, you can run directly from the meter to a fire pump controller and call it a day?
M mortimer third party inspector Location New England Occupation retired Nov 1, 2018 #1 So, you can run directly from the meter to a fire pump controller and call it a day?
M mortimer third party inspector Location New England Occupation retired Nov 2, 2018 #2 mortimer said: So, you can run directly from the meter to a fire pump controller and call it a day? Click to expand... HELLO. anyone out there?
mortimer said: So, you can run directly from the meter to a fire pump controller and call it a day? Click to expand... HELLO. anyone out there?
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Nov 2, 2018 #4 Assuming that the fire pump controller is listed as service equipment and assuming that the service conductors are installed per 695.6(A)(1), you can do that.
Assuming that the fire pump controller is listed as service equipment and assuming that the service conductors are installed per 695.6(A)(1), you can do that.