kwired
Electron manager
- NE Nebraska
- EC
Overcurrent protection on these lines is for protecting those lines, and not secondary wiring. If the protection device is a recloser, then you get a similar surge probably three times before the protective device remains open.The neutral for the primary, is the same as the secondary, so that should have blew out the pole fuse rather quickly. That's a direct to ground fault.
These conductors are not protected to tight levels that interior run conductors are typically protected, this is an attempt to allow for faults to burn clear instead of taking the line down which means less dispatching repair crews for minor incidents, and more system reliability from the consumers point of view.