Ah, not the POCO. Glad we agree on that now...............Not a matter of non-sinusoidal voltage generation by POCO. It is a matter of supplying from relatively weak power source.:slaphead:
Mods, this not bickering. It a serious and increasingly prevalent issue and it deserves to be better understood by many. I have been to a number of sites where there have been significant and costly failures.
@ Sahib. Voltage distortion of 7.5% is most certainly is something to be seriously concerned about. No, it isn't the POCO generating it. It is some customer causing it with probably large non-linear loads without a proper study of how they will interact with the supply that may be common with other users. The PCC or point of common coupling. Take heed. It may be to your advantage.
Another real life example. This was from a large paper mill in Kent, UK. We were installing some new DC variable speed drives. The power side was six-pulse phase controlled SCR bridges. Commissioning was a nightmare. Control of the firing angle for the SCRs used the supply to the drives. That supply had significant harmonic voltage distortion - of about the same order as than mentioned by the OP. The problem was that the new drives could not consistently determine the timing of zero crossing point.
My fix was to install a simple filter in the line that fed the timing circuit and make a small adjustment in the drive to compensate. Cheap to implement, very costly lost production time.
This is a long post by my usual standards. But I hope it serves to show, even if only by example, the nature of the issues and costs of harmonics