Hello,
I've got another motor calc that I have done and just want to make sure I am interpreting the code correctly.
We are going to be swapping out a old compressor for a new one. Details below.
Old compressor and circuitry.
5HP
23FLA
40c
RPM 1750
Ser Fac 1.15
#8 thhn on a 40amp qo standard trip beaker.
New compressor
7.5HP
FLA 33
40c
Rpm 1750
SF 1.15
According to 430.248
7.5HP = 44amps @ 208v
430.22 44 x 1.25 = 55Amps
Table 310.16 75c. 6 awg thhn
430.52.... Using Standard trip QO breaker.
Do we use the nameplate for the FLA or 430.248 FLC for the breaker?
If we use FLA then 33 x 300(non time delay)= 99 MAX (100) and 33x1.25 41.25 MIN (45) (per table 240.6)
Or if FLC 44 X 300 = 132 amp MAX
44 x 1.25 = 55 amp min
About a 200 ft run, VD 33amps at 208v 3.08% VD.
Plan on coming out of panel with 3/4 emt then switching over to 6/2 MC above grid ceiling then go up to the roof perlins and strap MC for about 130ft inside the garage then set a box and then go down the wall to disco, then flex over to compressor. I had planned on using a 45 amp breaker if we use fla or a 55amp breaker if we use flc for 430.52.
The motor has its own thermal overload.
Thanks!
I've got another motor calc that I have done and just want to make sure I am interpreting the code correctly.
We are going to be swapping out a old compressor for a new one. Details below.
Old compressor and circuitry.
5HP
23FLA
40c
RPM 1750
Ser Fac 1.15
#8 thhn on a 40amp qo standard trip beaker.
New compressor
7.5HP
FLA 33
40c
Rpm 1750
SF 1.15
According to 430.248
7.5HP = 44amps @ 208v
430.22 44 x 1.25 = 55Amps
Table 310.16 75c. 6 awg thhn
430.52.... Using Standard trip QO breaker.
Do we use the nameplate for the FLA or 430.248 FLC for the breaker?
If we use FLA then 33 x 300(non time delay)= 99 MAX (100) and 33x1.25 41.25 MIN (45) (per table 240.6)
Or if FLC 44 X 300 = 132 amp MAX
44 x 1.25 = 55 amp min
About a 200 ft run, VD 33amps at 208v 3.08% VD.
Plan on coming out of panel with 3/4 emt then switching over to 6/2 MC above grid ceiling then go up to the roof perlins and strap MC for about 130ft inside the garage then set a box and then go down the wall to disco, then flex over to compressor. I had planned on using a 45 amp breaker if we use fla or a 55amp breaker if we use flc for 430.52.
The motor has its own thermal overload.
Thanks!