- Lockport, IL
- Retired Electrical Engineer
Suppose I take two separate medium voltage utility sources (the two utility substations are miles apart), and connect them to a Main-Tie-Main switchgear. Each side "normally" supplies half the building. If one utility substation is lost, the switchgear automatically transfers the entire building to the other utility. The transfer takes less than 10 seconds, and I specify the switchgear to be "identified for emergency use," per 700.6. Am I done with all "emergency system" requirements of article 700? Do I even need to call one light an "egress light" and separate its circuitry from the nearby "non-emergency" light? Would the fact that the switchgear's transfer mechanism be serving all loads, normal and emergency, constitute a violation of 700.6(D)?
The client is trying to take credit for the second utility source, and wants to avoid having to buy a diesel generator.
By the way, before anyone asks what would happen if both utility sources were lost, let me pose the question of what would happen if the utility source were lost in some other building, and if that building's backup generator failed? Do we even have to design for the possibility that the backup source might fail?