construct
Senior Member
- Location
- Branson, Missouri
The second sentence states, "Emergency lighting systems shall be designed and installed so that the failure of any individual lighting element, such as the burning out of a lamp, cannot leave in total darkness any space that requires emergency illumination."
My scenario is a 4-story college campus building with classrooms and commons area. There is a standby generator that will start and restore lighting and selected loads if the entire building loses it's normal supply. If normal egress lighting branch circuit(s) fail on one floor or a portion of a floor, the standby system will not not come on, thereby leaving that area dark.
The architect says he has complied with 700.12. The first sentence states, "Current supply shall be such that, in the event of failure of the normal supply to, or within, the building........................."
I don't see that the within part has been complied with.
Your opinions or take on this would be appreciated. :?
My scenario is a 4-story college campus building with classrooms and commons area. There is a standby generator that will start and restore lighting and selected loads if the entire building loses it's normal supply. If normal egress lighting branch circuit(s) fail on one floor or a portion of a floor, the standby system will not not come on, thereby leaving that area dark.
The architect says he has complied with 700.12. The first sentence states, "Current supply shall be such that, in the event of failure of the normal supply to, or within, the building........................."
I don't see that the within part has been complied with.
Your opinions or take on this would be appreciated. :?