Two part question.
700.27 (new to the 2005 edition) says that for emergency systems, all overcurrent devices must be selectively coordinated with supply side overcurrent devices. That is hard to achieve, especially with branch circuit breakers in the instantaneous region.
Situation:
In a 400 amp panel, there is a 225 amp breaker serving a feeder to a 225 amp MLO panel. In the 225 amp MLO panel, there is a 20 amp breaker serving a branch circuit for emergency lights. I can get the two breakers in the upstream panel (i.e., the 400 amp main breaker and the 225 amp feeder breaker) to coordinate at all fault levels. I can also get the 20 amp branch circuit breaker to coordinate with the 225 amp feeder breaker, but not in the instantaneous region. There is, in fact, enough fault current available to risk having the fault cleared by the upstream 225 amp feeder breaker. The AHJ is adamant about enforcing the coordination rule throughout the range of available fault current.
Proposed Solution:
Install a fuse immediately downstream of the 20 amp branch circuit breaker. Use an in-line fuse (attach by wire nuts to the branch circuit conductors), not a fuse block (which would have had to be attached to the panel. I can easily achieve coordination. I would declare that the branch circuit?s overcurrent device is the fuse, not the breaker, and that the breaker is merely there to isolate the circuit for maintenance.
Questions:
1. Would you accept this proposal as meeting the requirements of 700.27?
2. Is it acceptable to use this type of fuse connection method internal to a panel?
p.s. If you like this solution, then it was my idea. If you don't like it, then it was my boss' idea, and I just told him I would post it for him. :grin:
700.27 (new to the 2005 edition) says that for emergency systems, all overcurrent devices must be selectively coordinated with supply side overcurrent devices. That is hard to achieve, especially with branch circuit breakers in the instantaneous region.
Situation:
In a 400 amp panel, there is a 225 amp breaker serving a feeder to a 225 amp MLO panel. In the 225 amp MLO panel, there is a 20 amp breaker serving a branch circuit for emergency lights. I can get the two breakers in the upstream panel (i.e., the 400 amp main breaker and the 225 amp feeder breaker) to coordinate at all fault levels. I can also get the 20 amp branch circuit breaker to coordinate with the 225 amp feeder breaker, but not in the instantaneous region. There is, in fact, enough fault current available to risk having the fault cleared by the upstream 225 amp feeder breaker. The AHJ is adamant about enforcing the coordination rule throughout the range of available fault current.
Proposed Solution:
Install a fuse immediately downstream of the 20 amp branch circuit breaker. Use an in-line fuse (attach by wire nuts to the branch circuit conductors), not a fuse block (which would have had to be attached to the panel. I can easily achieve coordination. I would declare that the branch circuit?s overcurrent device is the fuse, not the breaker, and that the breaker is merely there to isolate the circuit for maintenance.
Questions:
1. Would you accept this proposal as meeting the requirements of 700.27?
2. Is it acceptable to use this type of fuse connection method internal to a panel?
p.s. If you like this solution, then it was my idea. If you don't like it, then it was my boss' idea, and I just told him I would post it for him. :grin: