National Fire Protection Association
Electrical Engneenng, 1 Batterymarch Park, Quincy, MA 02169-7471 Phone 617-770-3000 • Fax 617-984-7070 • wwwnfpa org
August 30, 2007
Brian E. Rock Hubbell Inc.
Hubbell Technical Center 1613 State Street Bridgeport, CT 06605
Dear Mr. Rock:
Section 6-1.4 (a) of the NFPA Regulations Governing Committee Projects does not permit a formal interpretation that involves the determination of compliance of a design, installation, product or equivalency of protection. However, I can provide a staff opinion.
No, Section 700.9(B) of the 2005 NEC? specifies that the wiring of the emergency system from the emergency source or emergency source distribution overcurrent protection to the emergency loads is to be kept entirely independent (physically separated) from wiring of other systems, unless otherwise permitted in 700.9(B)(1) through (4). Therefore, based on the definition of entirely (see Webster's) one channel of a multi-channel raceway is not completely independent from the other channels, due to the physical connection (divider) to the adjacent channels.
Additionally, a multi-channel raceway is a raceway with a divider (not physically separated) - not multiple raceways (physically separated), which is further clarified based on 386.70 and 388.70 "combination raceways" (ones used for signaling and lighting) specifically. Providing the channels were separate raceways, 386.70 and 388.70 would not need to specify the permitted use of separate compartments of surface raceways as a means of separation of signaling circuits from lighting and power circuits.
I hope this satisfies your concerns. Please understand that this has not been processed as a Formal Interpretation, it must be considered as my personal opinion. Please see the statement below.
Important notice! This correspondence is not a Formal Interpretation issued pursuant to NFPA Regulations. Any opinion expressed is the personal opinion of the author, and does not necessarily represent the official position of the NFPA or its Technical Committees. In addition, this correspondence is neither intended, nor should be relied upon, to provide professional consultation or services.
Very truly yours,
Mark Cloutier
NFPA Senior Electrical Engineer
MC/ch
James W. Carpenter, Chair, NEC-AAC Jim Pauley, NEC-AAC Julian R. Burns, Chair, NEC-P08 Thomas W. Wood, Chair, NEC-P13 Leona Nisbet 1-70-07-37