So @Gridtied, just to be clear...
The PV point of connection being in the downstream sub, no additional protection for the 3/0 feeder is needed. The most it can see is 150A one direction or 31.05A the other. This is why 705.12(B)(1) only applies to connections made "other than at the opposite end".