Coworker and I are having discussion about 705.12(D)(2)(3)(c). See following scenario.
A 200A, 120/240Vac, 1ph, 3W Service feeds 200A MB Meter combo with feed thru lugs to 200A MB Sub panel. The meter combo only has a couple loads lets say 50A/2P and a 15A/1p and the Sub panel is full. Is it possible to install PV 60A/2P CB in Meter combo using 705.12(D)(2)(3)(c).
Using the wording of the code: 50A + 15A + 60A = 125A
My Argument is that you cannot install the PV breaker in meter combo as you need to also account for sub panel overcurrent devices. Coworker's argument is that there will never be more then 200A since Sub panel has 200A MB.
Thoughts?
A 200A, 120/240Vac, 1ph, 3W Service feeds 200A MB Meter combo with feed thru lugs to 200A MB Sub panel. The meter combo only has a couple loads lets say 50A/2P and a 15A/1p and the Sub panel is full. Is it possible to install PV 60A/2P CB in Meter combo using 705.12(D)(2)(3)(c).
Using the wording of the code: 50A + 15A + 60A = 125A
My Argument is that you cannot install the PV breaker in meter combo as you need to also account for sub panel overcurrent devices. Coworker's argument is that there will never be more then 200A since Sub panel has 200A MB.
Thoughts?