TallTimber
Member
- Location
- Southern Illinois
- Occupation
- Electrical Engineer
I have been dealing with some residential installations utilizing PCS protection of main service panel. The issue I am having a hard time making a decision on is if the PCS supply limit can be 100% of the bus bar rating.
For instance one installation is a 200A MSP with a 200A 80% main breaker. Pretty cut and dry standard home install. Solar is landed on the lowest position in the panel and would not comply with any of the 705.12 sections. For this reason they have opted to implement PCS to curtail solar supply at the predefined limit. This limit can be set at 100% of the bus bar rating correct(200A)? The PCS is just taking the sum of supply currents and curtailing the PV when load reaches the PCS limit. I cannot see how allowing the solar to operate between 160A-200A would cause issues on the panel as in this range the solar would only be taking load off the main breaker. I feel like there are a lot of moving parts here but I cannot find a corner of this problem that leaves the panel in a worse position than not having any solar, or maxing out the 120% rule.
For instance one installation is a 200A MSP with a 200A 80% main breaker. Pretty cut and dry standard home install. Solar is landed on the lowest position in the panel and would not comply with any of the 705.12 sections. For this reason they have opted to implement PCS to curtail solar supply at the predefined limit. This limit can be set at 100% of the bus bar rating correct(200A)? The PCS is just taking the sum of supply currents and curtailing the PV when load reaches the PCS limit. I cannot see how allowing the solar to operate between 160A-200A would cause issues on the panel as in this range the solar would only be taking load off the main breaker. I feel like there are a lot of moving parts here but I cannot find a corner of this problem that leaves the panel in a worse position than not having any solar, or maxing out the 120% rule.