Can any worker open or close or reset a breaker in the main switch gear or do they have to be trained and wear ppe for that ? 480 volts.
Can any worker open or close or reset a breaker in the main switch gear or do they have to be trained and wear ppe for that ? 480 volts.
For the opening and closing of a breaker, I agree with what has been posted, but as for resetting a breaker the rules change. You can reset a tripped circuit breaker if you know the cause of the trip, e.g., motor tripped due to a jam, the jam was cleared. If the cause of the trip is unknown, then you cannot reset the circuit breaker until you have determined the cause of the trip. If you close into a fault, the circuit breaker may fail on the second fault and cause even more damage or trip the backup protection and you lose even more equipment then was lost on the initial outage.