I have a bunch of 120V contacts (will use THHN) and one RS485 signal that I need to wire between enclosures. Issue is I would like to run them in one conduit, if possible.
The RS485 will be run using Belden 3105A - 65% covered copper braid.
I'm looking at NEC 725.136 and the exceptions for having these signals in the same conduit.
I believe, and looking for your opinions, that it appears exception I2 I can run the Belden cable in the same conduit as the 120V contact signals using flexible tubing (some nylon wire loom) to cover the RS485 cable.
Do you agree?
I first thought the copper braid was enough to cover exception I1, but a CSA inspector disagreed.
Thanks for help.