kwired
Electron manager
- Location
- NE Nebraska
- Occupation
- EC
Right, been mentioned on this site many times before when selecting conductor size you need to basically figure two ampacities, one is based on termination ratings the other based on insulation ratings (which includes any applicable adjustments). If you get two possible sizes the larger conductor is what you must use.It doesn't unless the correction factor increases the conductor ampacity. It sets the maximum ampacity of any conductor connected to a termination to the ampacity shown in Table 310.15(B)(16)... in other words you can't use smaller conductors or apply a correction factor of greater than 1.
We don't adjust the termination rating, we do make adjustments when insulation is subject to different conditions.