electricbird
Member
- Location
- wv
- Occupation
- electrician
Tasked with hooking up a still, (istill), from the Netherlands. Nameplate says 3 x400vac, fla:83a ,60hz, supply fuse 90a, Phase: 3 phase +pe, 4 wire...Apparently European 3 phase is 400 volt. We have 240 3 phase here, ( line to line, with one high leg) They recommend 75 kva transformer 240 to 400, ( we are looking to get one from Maddox 240v Delta -400y 231 step up transformer. Calculations show 180 amps primary, 108 secondary. Issue: We have a 200 amp 3 phase panel, which I doubt you can find a 180 amp breaker for. 100 amp will not do, right?? Use a ocpd for the secondary side right?? Will we have to upgrade service/ panel for a 180 a breaker to feed transformer? I have seen other discussions about feeding with a 100 amp, but that was with higher voltage,(460?) I appreciate thoughts and expertise