Could someone help me find the load a 75 kva 3 phase transformer on 120/208 voltage can hold? It's been a while since I've had to do the calculation.
Thanks
Thanks
75000 / (208 x 1.73 ) = 208.3333
208 x 1.25 = 260.416
I wouldn't but I don't have to conform to your arcane rules..............Would you use 125% to determine the maximum load?
Here we go:
http://www.rapidtables.com/calc/electric/kVA_to_Amp_Calculator.htm
I got 208A first time around just didnt look correct.
Thanks for the quick reply. The reason I'm asking is that I've got a potential customer who already has a business on one side of their building, and wants to put a tanning bed business in the other side. They already have a 175 amp 3 phase panel in the building with no empty spaces, and wants me to wire 5 outlets for tanning beds. Each bed pulls 37 actual amps according to the specs they gave me. If I take each bed at $ 100% that is 185 amps. I'm not sure how long the beds run, but if they go over 3 hrs. I would have to figure for continuous duty, correct? Or is that only for the branch circuit? Can't remember now. But any way, the transformer feeding the business is 75 kva. According to your calculations, it would look like the transformer would have to be changed, and I would have to change the service from 200 amps to 400 amps. I'm assuming the service is 200 amp 3 phase right now. I have to go for another look today sometime. Any input on this would be appreciated.
Thanks
I don't think they would be allowed to be. Nowhere near.I can't imagine anyone would be in a tanning bed for 3 hours,
Thanks for the quick reply. The reason I'm asking is that I've got a potential customer who already has a business on one side of their building, and wants to put a tanning bed business in the other side. They already have a 175 amp 3 phase panel in the building with no empty spaces, and wants me to wire 5 outlets for tanning beds. Each bed pulls 37 actual amps according to the specs they gave me. If I take each bed at $ 100% that is 185 amps. I'm not sure how long the beds run, but if they go over 3 hrs. I would have to figure for continuous duty, correct? Or is that only for the branch circuit? Can't remember now. But any way, the transformer feeding the business is 75 kva. According to your calculations, it would look like the transformer would have to be changed, and I would have to change the service from 200 amps to 400 amps. I'm assuming the service is 200 amp 3 phase right now. I have to go for another look today sometime. Any input on this would be appreciated.
Thanks
Would you use 125% to determine the maximum load?
125% of what? OP asked about the load of a 75 kVA transformer- which is 75 kVA, breaks down to the already mentioned 208 amps per phase. Secondary protection typically can be 125%, most cases secondary conductor needs to be 125% if continuous load, but the designed rating of the transformer is still 208 amps and not an additional 25%, nor is it 80% of 208.yes and most engineers here size using 125 %
Notes:
1. Where the required fuse rating or circuit breaker setting does not correspond to a standard rating or setting, a higher rating or setting that does not exceed the next higher standard rating or setting shall be permitted.
Notes:
1. Where 125 percent of this current does not correspond to a standard rating of a fuse or nonadjustable circuit breaker, a higher rating that does not exceed the next higher standard rating shall be permitted.
but the designed rating of the transformer is still 208 amps and not an additional 25%, nor is it 80% of 208.
Commercial/residential isn't a factor in NEC, rules of location of service equipment is general in nature and applies to all types of installations. You may have local rules that differ though. All NEC says is the service disconnecting means needs to be either outside or nearest the point of entry if inside, though that last part is interpreted in many different ways around the country.Maybe just one more question, kinda related to this post. Didn't want to start another one since I already had this one. I don't do much heavy commercial so I'm sorta confused on the idea of not having a main outside on a commercial service. The business I have talked about, has a CT can outside and a meter, but I see no kind of disconnect. Am I missing something here? I've seen other buildings like this. The sub panel ( or in this case would be the Main Panel) is about 10 or 12ft. away at least.
Thanks
Thanks for the quick reply. The reason I'm asking is that I've got a potential customer who already has a business on one side of their building, and wants to put a tanning bed business in the other side. They already have a 175 amp 3 phase panel in the building with no empty spaces, and wants me to wire 5 outlets for tanning beds. Each bed pulls 37 actual amps according to the specs they gave me. If I take each bed at $ 100% that is 185 amps. I'm not sure how long the beds run, but if they go over 3 hrs. I would have to figure for continuous duty, correct? Or is that only for the branch circuit? Can't remember now. But any way, the transformer feeding the business is 75 kva. According to your calculations, it would look like the transformer would have to be changed, and I would have to change the service from 200 amps to 400 amps. I'm assuming the service is 200 amp 3 phase right now. I have to go for another look today sometime. Any input on this would be appreciated.
Thanks