If they are 1ph to neutral, 37A on each leg x 5 = 74, 74, and 37. 3ph would be 175, 175, 175. L-L would be 111,111, 148 (I think - doing this in my head).
So
a) you need to know what the beds are wired for (120V, 208V 1ph, 208V 3ph)
b) what the existing demand is on the service
b) what size is the service
The POCO may not do squat about the 75kva xfmr that is there. The 50kva that serves this house and others is fed from a 20kV primary and a 75A primary fuse (yes, that's 1494kw) . They (Dominion) are obviously not worried about what loads are happening on the secondary side.
istm if one sat in a tanning bed for 3+ hours at full song, they'd be bbq. iow, they are not continuous loads.