I know the typical industry installation is to size the primary OCPD of a 75 KVA transformer at 125 amps and the Secondary at 300 amps. I currently have a set of drawings that is showing the Primary OCPD being sized at 90 amps and the Secondary at 200 amps. It looks like the designer sized these breakers and conductors to the load it will be serving rather than the size of the transformer. Is the designer ok by doing this, or should it be done at 125 amps and 300 amps.