To all, I have an industrial installation that requires a 755 volt rated breaker, 1600 amps, 25 kA SCI.
UL, CSA & IEC molded case breakers are all rated below this voltage.
Schneider Electric makes a IEC rated breaker that meets the system requirements.
The machine's manufacturer recommended the particular breaker. (NW16H10). The breaker will be installed separately from the existing machine.
1. Does IEC test molded case breakers or only set the standards to build the breakers?
2. This breaker model has not been tested by UL or CSA, therefore it is not listed or labeled by either agency.
3. By the NEC the electrical products are to be listed or labeled in order to be installed.
This product is neither listed or labeled so it looks like I cannot use it.
4. Does IEC list or label products, if they do is it acceptable in the U.S.?
5. Is there a list somewhere of IEC labeled or listed products?