I have a questions about 75KVA 480/208 3Ph transformer.
The transformer is feed circuit breaker on meter center on the first floor.
CB is sized 125A (75/0.831 x 1.25= 112.82A).
The distance from meter center to transformer is about 120'.
I have some questions:
1. Can I locate the 75KVA transformer on the second floor above the suspending ceiling? Any special requirements for ventilation? Can the transformer be hang mounted? Is this possible?
2. Do I have to provide the main disconnect adjacent to transformer on the primary side? (I propose the transformer is protected by CB on the first floor)
On the second side I propose 3ph 225A MCB Panel.
Thank you in advance!