75KVA transformer protection
jamism
Hello Everyone,
I have a 75KVA 3 phase transformer (480V to 208V) 90A on the 480V side. I know I'm supposed to protect it up to 125% which turns out to be 112A. I want to use a 110A 3 pole breaker but is a 100A breaker still OK to use. I am worried about nuisance trips and the inrush current tripping breaker. What do you guys think is 100A good?
Thanks.
can't you go to the next higher standard size breaker? I am a big fan of installing the largest OCPD the code allows.
i might even be inclined to use the rule that allows for 250% in some cases, but in this case it might create an expensive solution.
In this part of the country, historically many 75KVA transformers have been protected at only 100A on the primary.
Where I am if an EE designs it the 75 KVA will have a 150 on the primary.
If an EC designs it there will be a 100 on the primary, I have never seen a problem with the 100.
The benefit of using a 100 is the fact a 100 amp breaker will fit in a panel where a 125 or 150 will not.
The make and model of the breaker and should also be considered. There are differences on trip characteristics, that inrush may factor in.