Have a customer who wanted to upgrade his current tankless water heater. He selects a Titan model, one which has a dataplate that says "2 40A breaker - (2 hots, 1 ground)" with an amperage reading for "77". Doesn't make much sense. I assumed it was only asking for basically one 8/2 romex on a 40 amp breaker. So we call the manufacturer to find out what's going on with this and the guy on the phone tells me I'm supposed to parallel 2 sets of #8 for 4 #8s altogether, and each cable should be on a seperate 40 amp breaker.
At this point I begin to explain to both the customer and the guy on the phone that there's a major problem here with what they're asking me to do, parallel (2) 40 amp breakers to create 80 and that it doesn't make any sense and violates all kinds of codes, 310.4 for starters. So I told my client to upgrade to the 60 amp instead of this mess.
If you know any other codes this violates post em.
At this point I begin to explain to both the customer and the guy on the phone that there's a major problem here with what they're asking me to do, parallel (2) 40 amp breakers to create 80 and that it doesn't make any sense and violates all kinds of codes, 310.4 for starters. So I told my client to upgrade to the 60 amp instead of this mess.