8 300kcmil Close enough?
More info, please:
Resi or commercial? Service, or feeder/branch? Copper or aluminum? What type of insulation? Any derating needed?
My first reaction is it's way too big. 300 copper is 240-320amps in T310.16.
natfuelbill said:
400A Main service breaker, copper, using the 75C THWN
THWN only? Not dual rated THHN?
OK,
300 CU @ 75 C = 285 amps
285 x 2 = 570 amps
Six current carrying condutors get reduced to 80%
570 x .8 = 456 amps
natfuelbill said:
The N will have the unbalanced and non-linear.
399 is not 400 .........
"Major portion" equals more than 50% nonlinear. And 399 is close enough if the connected load is 399 or less.
For a guy that is asking for help your making this hard.
Did you read the section I pointed out?
Is the major portion of the load non-linear?
And I asked for the calculated load back at the start for the same reason Dennis and Trevor mentioned it.
240.4(B) may help you out based on the load not the breaker.