mbrooke
Batteries Included
- Location
- United States
- Occupation
- Technician
Aren't these conductors protected at their source, the battery charger, at 50A, the 200 fuse is not part of their protection. Is this why you say they "don't count"?Line side tap, or the fact this is a substation battery charger and doesn’t count.
I guess you would have a fit to find out S&C motor operators have slugs installed in them rather than fuses..
Line side tap, or the fact this is a substation battery charger and doesn’t count.
I guess you would have a fit to find out S&C motor operators have slugs installed in them rather than fuses..
Ask the battery people. Batteries can pump out a lot of current in a dead short situation but it is unlikely to be tens of thousands of amps.I can do that; I assume the batteries deliver the power, and exclude the charger.
Question- how do I find out the short circuit output of a battery bank?
What’s the amp hour of the bank?I can do that; I assume the batteries deliver the power, and exclude the charger.
Question- how do I find out the short circuit output of a battery bank?
90Aren't these conductors protected at their source, the battery charger, at 50A, the 200 fuse is not part of their protection. Is this why you say they "don't count"?
that and 99.2(b)Aren't these conductors protected at their source, the battery charger, at 50A, the 200 fuse is not part of their protection. Is this why you say they "don't count"?
That’s the charger circuit and it’s the way substation battery charger systems are generally wired.Ask the battery people. Batteries can pump out a lot of current in a dead short situation but it is unlikely to be tens of thousands of amps.
P.S. - what makes you think you can run cord from the charger to the 200 A disconnect?
He seems worried about meeting code as far as the tap goes so why wouldn't he worry about the proscriptions on using cord.That’s the charger circuit and it’s the way substation battery charger systems are generally wired.
Either that or direct to battery bank bypassing the disconnect, with a separate disconnect in the charger.
Typo and not paying attention... 99.2(B) was a screwup90.2(B)
that and 99.2(b)
Standard run of the mill drawing off the internet.I have to ask for the specs on the individual batts as they are not in the bill of materials price list (yet), but here is what the plan drawing shows:
View attachment 2557207
Another question:I can do that; I assume the batteries deliver the power, and exclude the charger.
Question- how do I find out the short circuit output of a battery bank?
Standard run of the mill drawing off the internet.
Another question:
Why do you need to know?
90.2 is only applicable if this installation is a 'utility. I have designed and commissioned station battery systems like this for customer substations subject to the NEC.90
.2(B)
that and 99.2(b)
90.2 is only applicable if this installation is a 'utility. I have designed and commissioned station battery systems like this for customer substations subject to the NEC.