Hi all,
Been a while since I have posted.
I have a small disagreement with a fellow contractor. The question at hand is
Is it compliant to use #8 THHN on a 50 amp breaker given the de-rating due to continuous load as we must follow her in CA?
Oh and the length of the run is under 90 feet so voltage drop should be fine.
Thanks
Many chargers are running at 48 amps so 48 x 125% = 60 amps. That means you need 60 amp overcurrent protective device and 60 amp wiring. With NM cable you are restricted to the 60C column otherwise you can use 75C
If the chargers runs at 40 amps then 125% x 40 = 50 amp. You need a 50 amp overcurrent protective device and conductors.