I understand how you are interpreting the requirement(s)... and I'll not say it is totally wrong... but you'll have to cite other definitions and requirements which back up your interpretation in order for me to say you are totally correct. Under the NEC, only service and tap conductors can be protected by a load-end OCPD. In all other cases, the OCPD only protects conductors on the load side of the OCPD.
Happy holidays and merry Christmas to you and yours...
Acually reasonable doubt mght be good enough - bear with me-----
240.21 Location in Circuit
Overcurrent protection shall be provided in each ungrounded circuit conductor and shall be located at the point where the conductors receive their supply
except as specified in 240.21(A) through (H). Conductors supplied under the provisions of 240.21(A) through (H) shall not supply another conductor except through an overcurrent protective device meeting the requirements of 240.4.
Any where in 240.21(A)-(H) the OC can be located on the load side of the conductors.
(A) Branch-Circuit Conductors. Branch-circuit tap conductors meeting the requirements specified in 210.19 shall be permitted to have overcurrent protection as specified in 210.20.
Branch Circuit, Individual. A branch circuit that supplies only one utilization equipment.
Tap Conductors. As used in this article, a tap conductor is defined as a conductor, other than a service conductor, that has overcurrent protection ahead of its point of supply that exceeds the value permitted for similar conductors that are protected as described elsewhere in 240.4.
Both definitions apply to 240.21(A) and the OP design.
240.4 Protection of Conductors
Conductors, other than flexible cords, flexible cables, and fixture wires, shall be protected against overcurrent in accordance with their ampacities specified in 310.15, unless otherwise permitted or required in 240.4(A) through (G).
(B) Overcurrent Devices Rated 800 Amperes or Less.
The next higher standard overcurrent device rating (above the ampacity of the conductors being protected) shall be permitted to be used, provided all of the following conditions are met:
(1) The conductors being protected are not part of a branch circuit supplying more than one receptacle for cord and
plug-connected portable loads.
(2) The ampacity of the conductors does not correspond with the standard ampere rating of a fuse or a circuit breaker without overload trip adjustments above its rating (but that shall be permitted to have other trip or rating
adjustments).
(3) The next higher standard rating selected does not exceed 800 amperes.
Saitsfies protection described in tap conductor definition per OP design.
210.19 Conductors ? Minimum Ampacity and Size
(A) Branch Circuits Not More Than 600 Volts.
(1) General. Branch-circuit conductors shall have an ampacity not less than the maximum load to be served. Where a branch circuit supplies continuous loads or any combination of continuous and noncontinuous loads, the minimum branch-circuit conductor size, before the application of any adjustment or correction factors, shall have an allowable ampacity not less than the noncontinuous load plus
125 percent of the continuous load. Meets the requirement of 240.21(A) per OP design.
210.20 Overcurrent Protection
Branch-circuit conductors and equipment shall be protected by overcurrent protective devices that have a rating or setting that complies with 210.20(A) through (D).
(A) Continuous and Noncontinuous Loads. Where a branch circuit supplies continuous loads or any combination of continuous and noncontinuous loads, the rating of the overcurrent device
shall not be less than the noncontinuous
load plus 125 percent of the continuous load.
Meets the requirement of 240.21(A) per OP design.
(B) Conductor Protection. Conductors shall be protected in accordance with 240.4.
Flexible cords and fixture wires shall be protected in accordance with 240.5.
Full circle to previous post ---
Overcurrent Protective Device, Supplementary. A device intended to provide limited overcurrent protection for specific applications and utilization equipment such as luminaires and appliances. This limited protection is in addition to the protection provided in the required branch circuit by the branch-circuit overcurrent protective device.
The definition of
supplementary overcurrent protection device makes two important distinctions between overcurrent protective devices. First, the use of a supplementary device is specifically limited to a few applications. Second, where it is used, the supplementary device must be in addition to and be protected by the more robust branch-circuit overcurrent protective device.
240.5(A) states; Supplementary overcurrent protection, as covered in 240.10, shall be permitted to be an acceptable means for providing this protection.
and the way 240.10 reads it is not replacing the requirement but protecting as if it were the OC.
A device intended to provide limited overcurrent protection for
specific applications and utilization equipment -- some SOC are intergal to equipment as the OP is stating in which the supply cord cannot be on the load side of SOC. There can never be a load from the individual unit that can exceed the SOC rating. I do get your point but the reason for using the SOC as
the wire protection for cords does appear to be a specific application.
I do see a path thru code -- I could have missed something here and await the crossfire --