SparkyV
- Frederick MD
- Electrician
I have a couple questions about wiring for an 80 amp shower steam generator.
The unit itself draws 63 amps total at 240 volts.. This means that a 4-2 romex/NM sheathed cable with ground should suffice correct? 334.80 states ampacity shall not exceed that of a 60 degree rated conductor and the 90 degree rating shall be permitted to be used for ampacity and adjustment and correction calculations provided the final derated ampacity does not exceed that of a 60 degree rated conductor. 63 amps is below the 70 amps per 60 degree column which calls out 4 wire.
Also would using SE wire achieve anything different in regards to using the 75 degree column or does 338.10.B.4 put me right back into the 60 degree column.
Any help would be greatly appreciated. Thanks for taking time to look at the questions.
-Vince_
-Vince_