fireryan said:Thanks 480
jim dungar said:The NEC uses the term 125% not 80% when describing loading of overcurrent protective devices.
elvis_931 said:So does that mean for example that a 100amp breaker can have an actual load of 125amps?
elvis_931 said:So does that mean for example that a 100amp breaker can have an actual load of 125amps?
Unless otherwise marked, circuit breakers should not be loaded to exceed 80 percent of their current rating, where in normal operation the load will continue for three hours or more.
iwire said:ALL breakers and fuses are designed to be used at 100% non-continuously, that is less then 3 hours straight.
For loads that are continuous the NEC requires the conductors and the overcurrent protection to be sized at 125% of the load. Which results in a breaker that is not loaded more then 80%.