jimday
Member
- Location
- Northern California
At the risk of sounding or being stupid, I can't seem to find a reference to 80% rated breakers other than 215.2(A)(1) under the exception where is states that the assembly (including the circuit breaker) must be rated for the continuous load. The only other section is 230.208(B) where it states that the restriction to 80% of the breaker rating does not apply for continuous loads for protective devices installed insystems over 600V. Is there a specific section that addresses this without "dancing" about?
Thanks!
Thanks!