800 A service

Status
Not open for further replies.

AndyA

Member
Location
Ash092275
Occupation
Electrician
I’m working on 3ph 800A 120/240 service
I ran 2 4” conduits underground total wire run we’ll be 120’. What size aluminum wire can I use
 
Why did you run the conduit before you checked the wire size? That is risky

Your choices are 4 parallel sets of 300 kcm with 2 sets in each conduit which will give you a total of 736 amps. So if the calculated load is 736 or less you could connect to an 800 amp breaker.

For a full 800 amp service you need 4 parallel runs (2 in each conduit) of 350 kcm

I didn't check to see if they would fit but it seems it will.

Edit...
I made some error in my math but I can't even duplicate it so I must have typed in the incorrect number... Infinity has the correct answer below.
 
Last edited:
I’m working on 3ph 800A 120/240 service
I ran 2 4” conduits underground total wire run we’ll be 120’. What size aluminum wire can I use
Is that a high-leg delta? (Neutral and high leg could be smaller)

Metal or PVC conduit? (Metal could be EGC)

Service or feeder? (Will there be an EGC?)

My calc shows that eight 400s will fit in a 4" PVC conduit.
 
I think my best bet is to run 500MCM copper
Is that a high-leg delta? (Neutral and high leg could be smaller)

Metal or PVC conduit? (Metal could be EGC)

Service or feeder? (Will there be an EGC?)

My calc shows that eight 400s will fit in a 4" PVC conduit.
no High leg. Running 4” PVC
 
Hope you already have the gear, I’m looking at almost 10 months lead time for an 800 amp fusible 600 volt disconnect, and an 800 amp 277/480 three phase MB panelboard. Found two new 800 amp disconnects at a salvage place in Wisconsin, so instead of a 800 amp panelboard, I’m doing a wireway with off the shelf disconnects. Got to have the engineer re-draw it for the inspector.
 
Hope you already have the gear, I’m looking at almost 10 months lead time for an 800 amp fusible 600 volt disconnect, and an 800 amp 277/480 three phase MB panelboard. Found two new 800 amp disconnects at a salvage place in Wisconsin, so instead of a 800 amp panelboard, I’m doing a wireway with off the shelf disconnects. Got to have the engineer re-draw it for the inspector.
Yes I have everything ready and mounted. Had to shop all over on line to collect it all.
 
Why isn't this engineer specifying the conductors?
Good question. And if he wants the full 800 amps then the installer will have to provide it. Since he already install the equipment he might be limited as to the wire size and how many sets he can actually use.
 
He is asking for two sets of 500
Wanted to see if going aluminum we’ll be better price
If he specked 500 CU that is what he wants. If he does allow you to go with AL he'll probably be wanting a credit for the customer.
 
The gear will probably only have double lugs, triple is special order. My engineer specs three sets of 300 kcmil AL. I probably need to go back and have him change it to two sets of 750. I haven’t ran any pipe yet because it took so long to get the prints.
 