Context:
I need an 800 (or 760) Amp Distribution Block for a panel to be rated at 35kA
The panel will be fed from an 800 Amp Circuit Breaker in the MDB about 10 feet away with 2 x 500
Total load in the panel will be 560 Amp with the largest load being 77 Amp
Need a little spare capacity above the 560 Amp of at least 100 Amp for some future additions
Problem:
Can not find a suitable Distribution Block.
All the Distribution Blocks I can find are only rated above their nominal 5 or 10kA when used in conjunction with 600 Amp Type J Fuses or a specified 600 Amp Circuit Breaker or similar, but nothing greater than 600 Amp
Question:
Any recommendations for a solution ?
And would a configuration as shown in the image work ?
And if it would work, would it still work without linking the two Distribution Blocks ?
I need an 800 (or 760) Amp Distribution Block for a panel to be rated at 35kA
The panel will be fed from an 800 Amp Circuit Breaker in the MDB about 10 feet away with 2 x 500
Total load in the panel will be 560 Amp with the largest load being 77 Amp
Need a little spare capacity above the 560 Amp of at least 100 Amp for some future additions
Problem:
Can not find a suitable Distribution Block.
All the Distribution Blocks I can find are only rated above their nominal 5 or 10kA when used in conjunction with 600 Amp Type J Fuses or a specified 600 Amp Circuit Breaker or similar, but nothing greater than 600 Amp
Question:
Any recommendations for a solution ?
And would a configuration as shown in the image work ?
And if it would work, would it still work without linking the two Distribution Blocks ?