zach.bes
- Porterville
Hey everyone,
Just passed my CA Journeyman test and have a lot more responsibility. And I like to do things correctly so I figured I would consult with the experts.
I'm installing (2) 800A 480V MLO Breaker Panels that are fed from a 2000A Main service switchgear (Protected via 800A breakers of course) and the boss and I have been going back and forth in regards to properly grounding/bonding these panels.
Each panel is fed via parallel 600MCM with 1/O EGC's. The panels are roughly 12ft from the structure I-beams (grounding electrode).
What do we need to do to properly and safely ground/bond these panels?
Boss says 1/O bond to I-Beam
I say 3/O bond to I-Beam. Using formula from 2014 NEC 250.102
I also don't think we need to bond these AT ALL to the I-Beam since they are sub panels. We don't want objectionable current, right?
What are your thoughts?
I'm new to this so forgive my lack of knowledge.
I always keep my 2014 NEC with me but it can be confusing at times.
Thanks.
Zach
Thanks.
Zach