800A 480V Breaker Panel - Bond to structure or not?
zach.bes
Porterville
Hey everyone,
Just passed my CA Journeyman test and have a lot more responsibility. And I like to do things correctly so I figured I would consult with the experts.
I'm installing (2) 800A 480V MLO Breaker Panels that are fed from a 2000A Main service switchgear (Protected via 800A breakers of course) and the boss and I have been going back and forth in regards to properly grounding/bonding these panels.
Each panel is fed via parallel 600MCM with 1/O EGC's. The panels are roughly 12ft from the structure I-beams (grounding electrode).
What do we need to do to properly and safely ground/bond these panels?
Boss says 1/O bond to I-Beam
I say 3/O bond to I-Beam. Using formula from 2014 NEC 250.102
I also don't think we need to bond these AT ALL to the I-Beam since they are sub panels. We don't want objectionable current, right?
What are your thoughts?
I'm new to this so forgive my lack of knowledge.
I always keep my 2014 NEC with me but it can be confusing at times.
Thanks.
Zach
All that you need is the EGC within the feeder. You can bond it to the steel if you want but it's IMO a waste of time and money.
To add to what Infinity posted.
The I beam should have already been bonded from the MDP or switchgear.
If used as part of the GES, it would be a 3/0 using T250.66.
If just be being bonded it would be a 3/0 using T250.102(C)(1), which you posted above, using the formula from note 1. This a supply side jumper from the MDP.
However, if you ran a jumper from the sub panel to steel this just be an extraneous/unneeded load side jumper and 250.102(D) says use T250.122 which gives you a 1/0.
As a point of conversation, note that 250.136(A) states the the metal frame of the building can not be used as an equipment grounding conductor so IF you elect to install a bond to the steel, you would still need to provide an equipment ground meeting the requirements of 250.118,
Here is what I'm dealing with. Thanks everyone.
Zach
We wasted time and money. But not much. Already had a scrap piece of 3/O with my crew. If it were completely up to me I wouldn't bond at all, but boss wanted it bonded so I said if we are bonding at all we should 3/O.
Welcome to the forum. Gratzon passing your test. I see your question has been resolved, tho I wanted to address one point:
You do not want more than one path for the neutral from panel to subpanel. You have no neutral feed here anyway, which begs the question (again): what are the small white wires in the bottom of the cabinet? You cannot remark white wires to be ungrounded conductors unless they are part of a cable assembly.
Equipment grounding conductors look a little small to me. That's some pretty small green wires for those two big conductors per phase.
If your "subpanel" is in a separate building or structure then you need to establish a grounding electrode system in that other building/structure. If your subpanel is in same building/structure as where it receives it's supply from then you should already have a grounding electrode system at the building service/main disconnecting means.
That's what I thought.
1/O EGC per pipe was code for parallel 600mcm's. I would state which one if I had it on me right now.
EGCs are sized according to the OCPD protecting the phase conductors.
For parallel conductors a full sized EGC must pulled in each conduit per 250.122(F), a 1/0 CU in your case for a 800A OCPD per T250.122