Ok I have a 800A 120/208V 3P4W 10KAIC MDP to install. The prints are telling me I need 6- 3 1/2" conduits with 4- 500MCM in each conduit. Thats a total of 24- 500MCM to go into this panel. Each conduit is 200' long. That is a total of 4800 feet of 500MCM at $8.33 this is $39,984.00 + Tax. Hell im not even sure where to put all the wire. By my calculations I should only need 3- conduits with 4- 500MCM in each one. Hell I think even 3- conduits with 4- 350MCM in each would deliver the 800A required.
Ok where am I going wrong here? I either have prints by a crackhead electrical engineer or I am missing something. The best part is I tried to contact the engineer and he is no longer in business.
I keep coming up with a min. of 4- 2/0 per phase for my calculations. I also derated the wire by 80%.
Ok where am I going wrong here? I either have prints by a crackhead electrical engineer or I am missing something. The best part is I tried to contact the engineer and he is no longer in business.
I keep coming up with a min. of 4- 2/0 per phase for my calculations. I also derated the wire by 80%.