800A Transfer switch, wrong lugs

Status
Not open for further replies.

templdl

Senior Member
Location
Wisconsin
Here is a PDF I found on a Cummins ATS.
on page 9 is the lug information. What the OP has is what it comes with for an 800 amp switch.
It also tells you to contact the factory for other lug options.

https://powersuite.cummins.com/PS5/...et/pdf/Commercial/Transferproducts/s-1270.pdf

Thanks. It looks as if he may be refering to 500kcmil as I don't see 400. But there is a a lug for (4) 600kcmil and I'm surprised that the OP didn't see that or that his rep didn't point that out.
But, it also must be confirmed that the enclosure has the room for the bending radius required for 600 and that the bus has the mounting holes for it.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
I always smile when on OP can be simply answered in one or two replies if only enough details were included in the first place such as the manufacturer of the ATS. But I must admit it does add to the intreque when everyone guesses as to who the manufacturer is.
Jumping to conclusions is the only exercise I get lately...
 