resistance
Senior Member
- Location
- WA
All checks out well at the main panel. The poco will check there side.
When you checked the voltage at the main, did you check at the output of the breaker feeding the motor. Maybe you have a loose connection at the main, I would pull the breaker and check for burning on the bussing and then switch the two phase conductors, then see if you have 100v on the other wire. If so the problem is in the main, if the problem follows the conductor then it is the conductor or a splice in the conductor.
Charlie,The current through the motor is not the issue. A difference in voltage from each hot leg to ground, as measured at the motor's location, is the issue. A lost neutral at the panel can cause the two voltages at the panel to become different from each other, as measured to the neutral/ground point at the panel. That would in turn cause a difference in voltages throughout the system.
Agreed. But that is not the issue at hand; we are not talking aobut line to line voltage. The OP speaks of L1 to EGC and L2 to EGC.I don't see that as changing the line to line voltage at the motor. The motor does not see the line to neutral voltages.