Back in the late 70's-early 80's I worked for a cable company doing, among other thing customer installs and service. They supplied us with a box of 4 foot long X 3/8" ground rods to pound in the soil for the ground from the ground block where the cable enters the house. I knew it was not NEC compliant and told them so but they didn't care. As cable grew word got around that they needed to be NEC compliant as far as grounding so some engineer in the company bought a copy of the NEC. After reading it for maybe a half hour he came up with 8' ground rods, cold water pipes and bonding to the service mast. All out of context because the NEC isn't like reading a Victoria's Secret catalog. You need some knowledge to understand it and without knowing how the book is written and what it covers you have no idea how to interpret what it says.
As an example see 250.94-
Bonding for Other Systems
An intersystem bonding termination for connecting intersystem
bonding conductors required for other systems shall be
provided external to enclosures at the service equipment or
metering equipment enclosure and at the disconnecting
means for any additional buildings or structures.
These "ground blocks" have been required since the 2011 Code cycle for cable and telephone to connect their grounds. I have yet to see one used.
The only company that had their act together was the old Bell System. All of their procedures were carefully engineered and documented in what they called their Practices. Every employee got a copy relevant to their job and it was followed to the letter. But alas, after the 1984 breakup everything went to hell and what's done today could be anything.
Utilities like cable and telephone and even satellite can get away with doing anything they want because there is no enforcement. While they are supposed to follow the NEC, unless it's new construction with premises wiring nothing is inspected.
-Hal