Roger Desi
- USA Florida
We have purchased the Fluke 1625 ground test meter and was testing/learning how to use it on our grounding system here at the shop.
Let me explain the best I can on where we conducted our test.
We have a computer room, and in this computer room we have a 208 volt 3 phase lighting panel, 1 computer, 1 small UPS system, 1-208v xformer (powering the UPS system) and phone service. In the corner of this room is a 10 foot ground rod. This ground rod has a #4 solid copper wire attached to a multi hole ground bar. There is a #6 green copper wire coming from the 208volt 3 phase panel ground bar and is attached to the multi hole ground bar. We have the 208volt xformer the UPS and phone service grounds attached to the multi hole ground bar as well. We have two clamps on the 1625 fluke meter, one clamps around the ground rod itself and the other clamp, clamps to the #4 soild at the multi hole ground bar with both clamps facing the proper direction (which is the stackless method)and the results of the test is 83 omhs. We know that is a very high reading, so we selected another ground wire (#8 green) about 4 inches away that is grounded to the same ground bar but goes to the UPS system our results were 0.061 ohms.Keep in mind that the #4 bare copper wire that goes to the ground rod was never disconnected. How can the two test be so different when they are using the same ground loop and the length of the wires are the same? Also the 208volt 3 phase panel is a sub panel for the computer room. I could use some help on understanding what is going on or what I might doing wrong.
Thanks,
Roger
Thanks,
Roger