83 percent rule for single family dwelling

Status
Not open for further replies.

rapidelec

New User
Location
Louisiana
Occupation
Electrical Contractor
I'm a little bit confused on where to apply the 83 percent rule. In the 2020 code book, 310.12 (B) talks about applying the 83 percent rule to feeders in dwelling units. Does this mean, that if I am adding a 100 amp sub panel to a 200 amp service main panel, that I can run #4 THHN (which is 85 amps in the 75 degree column) and put it on a 100 amp breaker?
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
No. The rule only applies to the total connected load. Once you run to a feeder the diversity no long applies that allows the 83 % rule
I would just say the rule doesn't apply because that's what the rule says.

I'm not very convinced there is any coherent reasoning behind it.

(Here's a common example that illustrates my point: A existing service consists of a 100A service disconnect feeding a subpanel inside the house with 4awg cu. This has always been fine at 100A because it's mostly 15-20A breanch circuits, plus an oven (or dryer). Owner wants to upgrade the outside disconnect to a 200A panel in order to add EV charger, heat pump, and electrify the dryer (or oven). Does the new subpanel breaker have to be downsized to 90? Yes. Why? Because the rule says so, no other logical reason.)
 
Last edited:

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
The logical reason is diversity. The CMP understands the reason and this rule has been in the NEC for over 50 years
But make a pubic input for the 2026 NEC. Often a public input allows the CMP to explain the reasoning.
 
The logical reason is diversity. The CMP understands the reason and this rule has been in the NEC for over 50 years
But make a pubic input for the 2026 NEC. Often a public input allows the CMP to explain the reasoning.
Usually all they will do is say "proposer has not provided evidence that.....". Even though the rule trying to be changed has no evidence or substantiation or no one can remember what it was. They love throwing that out there to deny things yet half the things in that book have no substantiation or are not even based on electrical theory....🙃
 

AC\DC

Senior Member
Location
Florence,Oregon,Lane
Occupation
EC
Usually all they will do is say "proposer has not provided evidence that.....". Even though the rule trying to be changed has no evidence or substantiation or no one can remember what it was. They love throwing that out there to deny things yet half the things in that book have no substantiation or are based on electrical theory....🙃
Just come up with something you can market and sell then a new rule
Will be passed to benifit you.
Sounds like the government
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
In his example the diversity has not changed.
The load on the 100 amp is still the same existing feeder is still the same
Exactly. The load has not changed at all. Thank you.

By the diversity logic, 310.12 should simply apply to all feeders of the applicable sizes in the covered occupancies.
 

mtnelect

HVAC & Electrical Contractor
Location
Southern California
Occupation
Contractor, C10 & C20 - Semi Retired
Usually all they will do is say "proposer has not provided evidence that.....". Even though the rule trying to be changed has no evidence or substantiation or no one can remember what it was. They love throwing that out there to deny things yet half the things in that book have no substantiation or are not even based on electrical theory....🙃

According to Don, the CMP now use the word "Resolved" to turn down a proposal.
 

Tulsa Electrician

Senior Member
Location
Tulsa
Occupation
Electrician
If you look at .83% rule
Divide 75c by 90c
75/90= .83333 🤔
Just for fun.
Run the numbers carry load at 75c and allow for the round up rule and 240.6 on the 90c. 🤔

Remember just for fun
lets use 175 amp rated service.
175*.83= 145.25

CU @75 1/0 @ 150
CU@90 1/0@ 170 up to 175

AL @ 75 3/0@ 155
Al @ 90 3/0 @ 175

Try another one, 225
225*.83= 186.75
3/0 CU
4/0 Al

Another
400*.83=332
400 mcm CU
600 Al
 

mtnelect

HVAC & Electrical Contractor
Location
Southern California
Occupation
Contractor, C10 & C20 - Semi Retired
According to don, my two PI will have the same fate ... "Resolved".
 

Attachments

  • NATIONAL ELECTRIC CODE 2023 - Section 200.4(C) Proposed Amendment.pdf
    128.2 KB · Views: 3
  • NATIONAL ELECTRIC CODE 2023 - Section 200.6(A) Proposed Amendment.pdf
    57.3 KB · Views: 3