need some guidance 90.2 (b) 4 (not covered) installations of communications equipment under exclusive control of communications utilities does this apply to the service, mains and feeders as well
Exactly what i am experiencing the utility wants a connect code to release a meter however it is unclear to me where my Jurisdiction lies if they are exempt from the NEC what standard exactly is being used to inspect and what i look at ground rods, bonding and wire size at the service however is AIC labeling or compartmentalization of the Mains part of the enforcement??? Many of these pieces of equipment come with the meter on one side and a couple 20 amp breakers on the other with receptacles that are not GFCI protected which cannot be because the equipment being served cannot afford nuisance trips however the equipment while being listed is still in violation of the NEC 210.8(b)
Sent from my iPhone using Tapatalk
In my opinion all other electrical equipment down to the branch circuits it subject to the requirements of the NEC. The only things that is not covered it the communications equipment and wiring.(4)
Installations of communications equipment under the exclusive control of communications utilities located outdoors or in building spaces used exclusively for such installations