Hi guys,
Question:
Taking the 90-deg column from NEC Table 310.16 gives me a value for the wire (or wires). However, will I be limited by the 75-deg column ampacity even if I do not apply any derating factors (i.e. from table 310.15(B)(2) and/or temperature derating table) ?
If I derate by voltage drop only, will I be limited by the 75-deg column ampacity?
thanks ahead for any responses