PetrosA

Senior Member
I think I've changed some outlets after you, wondering why my grounds are tucked behind the metal box, or cut to a 1/2inch in the box.

Now that's uncalled for and rude. I asked a legitimate question that anyone who does enough old work will come up against. You will have the option to either charge such a high rate for the work that the customer will choose to live with the danger, or you can weigh options and find a safe, "next best" solution.

Let me ask you this, if that had been a two wire romex, would you have walked away from the job, or charged possibly $1000 or more to rewire the light from the panel (let's assume worst case scenario top landing in a 2 or 3 story victorian, not balloon framed, wallpaper and with three way switching)? Did you check the BX for ground? Are you sure it wasn't tapped with a porcelain grommet into knob and tube somewhere? (Judging by the age of the insulation, it could have been).
 
I turn the circuit off before I work. So I see the panel and wire types. I open the ceiling so I see the concealed wiring.
If it were a 2 wire romex.. an electrician from the past 4 decades or whatever would have installed it. if it was a knob and tube installation and i wanted to add something to it, that it would be a whole different estimate and job altogethor. I always test my work to prove it to my customers it is safe. if grounds dont exist in the circuit i make them exist at whatever price. that is why I am there. to make something function and function safely, for peoples safety and equipment safety. if making something slightly better at a lower price is desired, I dont wanna be involved. I will clean up what ive already opened up and bill for my estimate and go home and wait for a call.

anyway, the home owner stated to me the home was built in the 50's. a time when the BX used did not have the steel wire to wrap around the outer casing. but through bonding of boxes and ect. a ground is present.

I'm sorry, my comment about the cut off grounds was rude. Just contribute what your "next best" solutions are. so we can all know what options we have besides rewiring.
 

aline

Senior Member
Location
Utah
In my humble opinion, it's safer to cut the ground wire back so you don't mislead anyone into thinking they've got a ground when they don't. Your opinion?
I run across these where the ground wire is cut back so nothing can be attached to it.
I hate this.
Often times I'm running a new cable with ground to the first outlet in the circuit so I can ground all the outlets on the circuit.

If the grounds in all the outlets weren't cut back I could easily ground all the outlets by just running the grounded cable to the first outlet. Since the ground is cut back I now have to get a new ground wire to every outlet and not just the first one.

It would be better to label the ground wire as not being grounded.
 

ohm

Senior Member
Location
Birmingham, AL
Now that's uncalled for and rude. I asked a legitimate question that anyone who does enough old work will come up against. You will have the option to either charge such a high rate for the work that the customer will choose to live with the danger, or you can weigh options and find a safe, "next best" solution.

Let me ask you this, if that had been a two wire romex, would you have walked away from the job, or charged possibly $1000 or more to rewire the light from the panel (let's assume worst case scenario top landing in a 2 or 3 story victorian, not balloon framed, wallpaper and with three way switching)? Did you check the BX for ground? Are you sure it wasn't tapped with a porcelain grommet into knob and tube somewhere? (Judging by the age of the insulation, it could have been).

This thread has turned very interesting with the ground issue.

We've all been there and short of running an EGC to the outlet the Code seems to be staying clear of the issue.

It does state all EGC's (green or bare wires) in an outlet shall be tied together and if the outlet is metal the EGC should be tied to it.

Now if the outlet is a non-grounded receptacle, that circuit may be repaired or extended in a variety of ways using "ungrounded circuit" labels.
 
self grounding outlets with the metal tab and clip under the screw register with my tester as a ground when attached to a metal box fed with metal clad cable. Does anyone know if thats sufficient?
 

mivey

Senior Member
This thread has turned very interesting with the ground issue.

We've all been there and short of running an EGC to the outlet the Code seems to be staying clear of the issue.

It does state all EGC's (green or bare wires) in an outlet shall be tied together and if the outlet is metal the EGC should be tied to it.

Now if the outlet is a non-grounded receptacle, that circuit may be repaired or extended in a variety of ways using "ungrounded circuit" labels.
But is it an ECG if it is not used as an ECG? To me, it is just an extra, uninsulated wire. It does not do anything until the circuit is upgraded and I do not cut them off because I anticipate that one day the upgrade is probably going to happen.

I never investigated too much what the code says about it because it seemed like common sense. Of course, the code is not always about common sense.

OTOH, I guess common sense would say to label the wire, but I never thought to do that either.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Often times I'm running a new cable with ground to the first outlet in the circuit so I can ground all the outlets on the circuit.

If the grounds in all the outlets weren't cut back I could easily ground all the outlets by just running the grounded cable to the first outlet.
If the cables between receptacles contained EGC's, wouldn't the homerun, also?


Plus, if you protect these 2-wire outlets with a GFCI, you mustn't interconnect them with EGC's at all.
 

ohm

Senior Member
Location
Birmingham, AL
self grounding outlets with the metal tab and clip under the screw register with my tester as a ground when attached to a metal box fed with metal clad cable. Does anyone know if thats sufficient?

Art.250.8 (A) list 7 methods any of which is sufficient.

Your method is #5
 

ohm

Senior Member
Location
Birmingham, AL
But is it an ECG if it is not used as an ECG? To me, it is just an extra, uninsulated wire. It does not do anything until the circuit is upgraded and I do not cut them off because I anticipate that one day the upgrade is probably going to happen.

I never investigated too much what the code says about it because it seemed like common sense. Of course, the code is not always about common sense.

OTOH, I guess common sense would say to label the wire, but I never thought to do that either.

I do the same thing when wiring to a porceilan light socket (no ground connection) in a plastic box. I just leave 6" of bare copper in the box for the next time.
 

PetrosA

Senior Member
I hadn't thought of labeling the ground, but I will start to do that. My primary concern was that in this area (at least) people do a lot of their own "small jobs" like replacing receptacles. Unfortunately it's not unheard of to see grounded outlets that someone installed into a two wire circuit, especially since when they see a metal wallcase they somehow assume it must be grounded. For those that are more careful, I figured that cutting the ground wire back would at least deter them from putting a 3-prong outlet into the box.

I asked about the BX ground because a lot of the old Vics in this area have BX tied into K+T or in newer homes into a 2-wire romex (ex. to feed a heater), but if you're tester is showing a ground, you're probably ok. The one shock that I got in my career that almost killed me was from a BX sheath that was hot (ungrounded and shorted to the black) when I grabbed it to move it behind a newly framed wall with copper plumbing installed (which I had to reach through to get at the BX). Since that time I NEVER assume a BX is grounded.

As far as frustrating the next guy because my romex needs to be replaced, I guess I'd rather that someone who knows what they're doing take care of that when the time comes than have it on my conscious that I mislead someone into creating a greater danger. A couple of feet of wasted romex during a whole-house rewire isn't going to break the bank ;)
 

aline

Senior Member
Location
Utah
If the cables between receptacles contained EGC's, wouldn't the homerun, also?
Not when someone extends the circuit and adds outlets from the existing ungrounded ciruit which I find quite often.


Plus, if you protect these 2-wire outlets with a GFCI, you mustn't interconnect them with EGC's at all.
It's nice to have grounded outlets for your electronics and surge protectors.
It's also safer to have grounded outlets in my opinion.
I see no reason to cut off ground wires making them unusable in the future.
Mark them as ungrounded but don't cut them off.
 

aline

Senior Member
Location
Utah
As far as frustrating the next guy because my romex needs to be replaced, I guess I'd rather that someone who knows what they're doing take care of that when the time comes than have it on my conscious that I mislead someone into creating a greater danger. A couple of feet of wasted romex during a whole-house rewire isn't going to break the bank ;)
Replacing romex in a finished house can break the bank.
Fishing new wire in sheetrocked walls or tearing out the sheetrock isn't cheap.

Sometimes someone adds onto the home and the addition is fed from the existing ungrounded circuits. When the existing part of the home is upgraded in the future new circuits with a ground can be ran to the addition and the receptacles in the new addition will be grounded. If the grounds weren't cut off the romex in the new addition wouldn't need to be replaced.

Most homeowners will put in 3-prong receptacles regardless of whether or not there's a ground present.

I don't know about other electricians but I check my receptacles after installing them to verify proper wiring and grounding. If they're not grounded I'll either ground them or I'll put a GFCI receptacle or breaker in and label them ungrounded.

A friend of mine wired his garage. He fed the receptacles from an existing ungrouned circuit. He figured since the ground wires weren't connected to anything he would just cut them off. I later came out and installed a new sub panel in his garage. If he hadn't cut off the grounds I could have easily grounded all of his receptacles at this time. Instead I had to rewire the garage. Not a big deal since it wasn't sheetrocked but still an unecessary expense.
 
Last edited:

ohm

Senior Member
Location
Birmingham, AL
Art 406.3 (D) (3) (c) allows grounding-type receptacle(s) to be installed in 2 wire non-grounded circuits if: supplied through a GFCI and labeled "GFCI Protected" and "No Equipment Ground". A supply of these labels are supplied w/ every GFCI.

So, if a two wire un-grounded circuit runs all over a house and it would be a major chore to try to install an EGC or GFCI receptacles why not just install a GFCI breaker and label the covers?

BTW "An equipment grounding conductor shall not be CONNECTED between the grounding-type receptacles".

However, I would NOT cut any bare wires off short, in case an EGC ever gets run to the circuit.
 

PetrosA

Senior Member
I would draw a line between fixing and extending a two wire circuit. I definitely won't tap into a two wire romex for new stuff, whether it's a receptacle, light, smoke detector etc. At that point let the owner fork over the cash for the new work. I limit those "gray" repairs to where it would be cost prohibitive to run a new line back to the panel, like in the example I gave with the light on the third floor landing or to repair one line to an existing receptacle that's hard/costly to re-feed.

If I have two wire romex feeding, I won't feed three prong outlets, even with a GFI at the beginning. I've seen too many problems with UPS units, computers etc. when the ground is missing. Two wire gets two prong outlets on my jobs.
 