UL 414 (Standard for Meter Sockets) says in section 27.10.5:
Thanks,
Wayne
Are such meter sockets commercially available, either standalone, or as part of a meter/main? Or is this just an option that nobody makes?If a meter socket is intended for and has been tested for use with 90C ampacity-sized conductors on the line side of the meter socket in accordance with Exception No. 1 to 14.6, the meter socket shall be marked "Conductor sized for 90C may be used on the line side of the meter socket" or equivalent.
Thanks,
Wayne