My son works for a motel chain. He said the outside condenser is supplied by #10 conductors and a 35a breaker. He said the name plate shows 37 a max draw. I guess thats the same as full load amps. He says the breaker trips often. I told him I would check amps while running and if over 30 , I would run #8 conductors first.. If load is in the 20's a 50a breaker or even 2.5 times the load is ok for start load on a regular breaker. He doesnt know if the 35a is a time delay breaker or not . I also told him if the running load is much over the 37a max there is problem with the compressor,, Does this sound like good advise, Hey If I scew up its me but if I cause someone else to do it that bothers me more.