busman
Senior Member
- Location
- Northern Virginia
- Occupation
- Master Electrician / Electrical Engineer
I have an A/C compressor. Wired with 10/2, 40 foot run, two JB's from panel to disconnect. All splices seem fine. Unit is very old, but was recently checked twice by A/C company with nothing found wrong. Unit trips the CB about 5-10 seconds after starting (sometimes) and sometimes while running. Nameplate is FLA=18.6, MCA=24, Max Fuse/Breaker=40, LRA=109. It is on a 40 amp breaker with 40A time delay fuses in disconnect. The highest inrush current I measured was 210A and it quickly settled to about 16A.
The only problem I could find was a very old contactor that was buzzing. Is it possible for the contactor to create enough voltage drop to increase the running current to trip the breaker? Any ideas would be greatly appreciated.
Thanks as always.
Mark
The only problem I could find was a very old contactor that was buzzing. Is it possible for the contactor to create enough voltage drop to increase the running current to trip the breaker? Any ideas would be greatly appreciated.
Thanks as always.
Mark