191006-2225 EDT
hbiss:
Ran an experiment on an LED. With a 2% change in excitation of current which is the necessary way with an LED. I did not visually see a change in intensity even with a long pulse. This was a red LED. A full wave rectified signal was used.
By comparison the 15 W incandescent was noticeable with the 2% voltage change at my 60 mS duration.
.
I'm with StarCat. I don't know when and why so many companies stop using start caps on residential AC's. I'd rather get the factory parts than a universal "hard start". Make sure you have an "anti-recycle" time delay.
For the cost of a cap, a TD relay, and a high and low pressure sensor you can greatly increase the life expectancy of your central AC (I also favor an expansion valve over a piston)....and you can run it with a much smaller generator.
For problems like this I like to divide and conquer. For example, if you disconnect POCO and a 7.5 KW portable generator runs the AC fine and the clocks don't reset chances are high your problems are exterior to the house. This assumes you can reliably recreate the problem.
...you can greatly increase the life expectancy of your central AC (I also favor an expansion valve over a piston)...
I'm with StarCat. I don't know when and why so many companies stop using start caps on residential AC's. I'd rather get the factory parts than a universal "hard start". Make sure you have an "anti-recycle" time delay.
...I don't know when and why so many companies stop using start caps on residential AC's. I'd rather get the factory parts than a universal "hard start".....
I'm with StarCat. I don't know when and why so many companies stop using start caps on residential AC's. I'd rather get the factory parts than a universal "hard start". Make sure you have an "anti-recycle" time delay.
For the cost of a cap, a TD relay, and a high and low pressure sensor you can greatly increase the life expectancy of your central AC (I also favor an expansion valve over a piston)....and you can run it with a much smaller generator.
For problems like this I like to divide and conquer. For example, if you disconnect POCO and a 7.5 KW portable generator runs the AC fine and the clocks don't reset chances are high your problems are exterior to the house. This assumes you can reliably recreate the problem.