Is it permissible to run the air handler on the same circuit as the ac compressor? I've been through the section on ac code in the 2008 book but I did not see anything about air handlers. The 3 phase compressors FL draw is marked as 11 amps. Min branch circuit requirement is 15 amps and max is 25. I went with the 25. The air handler is single phase 208v FL marked as 2.2 amps. Am I good to go with running the handler off two legs of the compressor circuit, or is there some clause that doesn't allow it?