I think the "flicker" is more noticeable with the smaller conductors because the voltage dip lasts longer. The smaller wire limits the current and causes the motor to take longer to start resulting in a more noticeable flicker. When you increase the wire size, you increase the current flow and increase the voltage dip on the service conductors but the higher current flow is of a shorter duration.
That's an excellent way of putting it! As far as time, we are only talking about under 1/2 second at most. At startup, the compressor will still be drawing a factor over the running load. Just how much and for how long are caused by the actual compressor, its condition, and the refrigerant charge in the system.