westelectric
Senior Member
- Location
- westchester county, NY
I have an a/c condenser 3phase 208v with a fused disco. Hvac repairman told the building to replace the fuses because they dont look to good, whatever that means. I went to look at it and felt that they need more than new fuses. They need a new disco and new emt that actually connects to the sealtight not almost connects to it. So my question is do I have to put a fused disco or can I just put an exterior saftey sw. since its outside. The conductors ARE fused at the main panel. Also min. cir. amp is 89a and max fuse is 125a. #6's feeding disco and #8's load side in sealtight whip is what they have there now.