Re: A/C CONDUCTOR SIZING
WOW, I completely forgot about this post. I just read it now and saw all kinds of stuff that needed commenting on.
I apologize for bringing this one back 3 weeks later.
First of all, as Larry just asked. The circuit conductors from the branch circuit and/or beyond the fuses, will never see more than either the A/C unit can draw or the OVERCURRENT protection will allow. Whether that OCP is at the start of the circuit or at the almost end of the circuit. Current is the same in a series/loop. So either location still protects the conductors (Unless something is tapped off that feeder, but that is a different subject).
Since current is the same in a series, the Breaker at the panel will see the same current AND the in rush current that the fuses see.
If a HACR breaker is installed at the panel with a NON fused disconnect, then we size the breaker at 125% (440.52)
If a standard breaker is installed at the panel, and a FUSED (time delay) disconnect is used, then the breaker at the panel is considered the SHORT CIRCUIT and GROUND FAULT protection, and would be sized at not more than 175%, but if that doesn't allow for startup, then 225%.
I can explain that reasoning...
440.22 states that we need SCGF protection. SCGF can be accomplished by "a protective device".
440.52 states that time delay fuse(s) "shall be permitted" to serve as SCGF protection. It doesn't say shall or has to or is limited to. That is if there is no other SCGF protection in the circuit.
Therefore, conductor sizing, throughout the whole circuit, is based not on breaker size, but on the minimum circuit ampacity.
Breaker sizing and fuse sizing (any kind of breaker) is based on the motor full load current.
Bob, your quote:
As an example, think of a HVAC unit that has a labeled minimum circuit ampacity of 19.9 amps and a Maximum fuse size of 35 amps.
We could install a 60 amp fused disconnect with 35 amp fuses and the feeder breaker could be 20 amps.
IMO that would meet the minimum NEC requirements.
That said, in no way do I think that is a good design or one that would make for a happy customer.
It doesn't make sense. The feeder breaker CAN'T be 20 amps. The A/C unit would not start.
But there is nothing wrong with a 60 Amp breaker and #12's if the calculations and the rules are followed correctly (depending on breaker type and percentages), since conductor sizing and breaker sizing are not based on the same thing.